Hello friends, I have two S7-300 CPU 317-2 PN/DP models and I want to configure them in SWR mode. Is it necessary for the CPUs to be connected via the DP port? Can the two CPUs be connected via the PN port for redundancy ? Can someone guide me through the configuration? ------------------------------------------------------------------------------------------ |
Last edited by: Wit_Moderator at: 07/29/2024 09:58:22New subject after splitting |
|
7/28/2024 12:46 PM | |
Joined: 9/27/2006 Last visit: 11/16/2024 Posts: 12294 Rating: (2691)
|
Hello friend; Communication links for SRW redundant configurations must use communication processors (CPs), for Ethernet links you would need CP 343-1. For confirmation, open the link to the SWR manual already proposed in this thread. https://support.industry.siemens.com/cs/ww/en/view/1137637 Hope this helps, Daniel Chartier |