11/21/2012 1:32 PM | |
Posts: 11 Rating:
|
hi all i have problem with pt100 connecting to sm 334-0ce01-0aa0 how wiring this ? and how programing this to reading temperature ? best regard |
11/21/2012 2:26 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating:
|
Hello, Sorry the 6ES7334-0CE01-0AA0 Only can be used for voltage or current measurement. you need an external PT100 converter or a module capable of temperature measurement. Analog input module SM 331; AI 8 x 12 bit; (6ES7 331-7KF02-0AB0) Analog input module SM 331; AI 8 x RTD; (6ES7331-7PF01-0AB0) Analog input module SM 331; AI 2 x 12 Bit; (6ES7331-7KB02-0AB0) Regards, Marcjan |
Problem solved? |
|
11/21/2012 2:37 PM | |
Joined: 9/27/2006 Last visit: 7/13/2024 Posts: 12268 Rating:
|
Hello pooneh; Here is ^part of the description of the SM 334, from the following manual: SIMATIC S7-300 S7-300 Automation System Module Data Order number 6ES7334-0CE01-0AA0 Properties ● 4 inputs in one group and 2 outputs in one group ● Resolution 8 bits ● Programmable measurement type at each channel group – Voltage – Current ● Not programmable, measurement and output type defined by hardwiring
|
Last edited by: dchartier at: 11/21/2012 2:38 PMreally, Marcjan, I must learn to type faster! |
|
11/22/2012 2:04 AM | |
Joined: 5/28/2008 Last visit: 7/12/2024 Posts: 4511 Rating:
|
Hello, If you want to connect your PT100 directly to an AI module, you can use one of the following modules:
Otherwise, you have to follow sugesstions of MArcjan & dchartier. Hope this helps.
|
Ayman Elotaify |
|