Thank You experts. This is my solution for this machine and probably for the most of air compressor. The Q1 and Q2 outputs are responsible for star-delta motor start. The Q4 output is responsible for load/unload valve The Q3 output is the stop function. AI2 is for PT1000 temperature sensor Will be greate, if someone want or can improve this. Attachmentair_compressor.zip (314 Downloads) |