Hello Pawar The Great I presume the CP 5308 is actually a CP 530, correct? If so it is a so called (ancient!) SINEC L1 Bus and you will NOT be able to connect a (Siemens) HMI to it. The onlyway to add a latest generation Siemens HMI to an S5 is viaProfibus DP and for this the "easiest" way is to add an IM308C to youryour S5 (alternatively you could use a CP5431). Below are a few more links on this subject and I hope this helps: Connecting a Windows-based panel to an IM308C (SIMATIC S5) via PROFIBUS DP Connecting a Windows-based panel to the SIMATIC S5 (CP5431) via PROFIBUS DP SIMATIC HMI WinCC flexible 2008 Communication Part 1 |
Cheers |
|
5/17/2010 6:39 AM | |
Posts: 18 Rating: (0) |
Hi Mr.Fritz, Thanks for the reply. Actually I am using IM 308 but i quoted it wrong as CP 5308 Your reply seems helping.... Thanks again Regards Pawar |