4/15/2020 2:40 PM | |
Joined: 3/14/2008 Last visit: 8/10/2024 Posts: 2082 Rating: (931)
|
Hi, The concept CMT and also EMT/EPHT works with master library that must be used. From there you create your types and with the Synchronize editor , you can synchronize your types to the project. You can reach the synchronize editor via: Plant View->Right click AS project->Plant Types->Synchronize. |
Last edited by: Oreca at: 04/16/2020 08:28:04Removed reference to XMLTRANSFER due attention of Heisenberg2 If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to2 thankful Users |
4/16/2020 7:36 AM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (217) |
Hi Oreca,
are you sure that you need to install the XML if you only use PCS 7? With regards |
This contribution was helpful to1 thankful Users |
4/16/2020 8:15 AM | |
Joined: 3/14/2008 Last visit: 8/10/2024 Posts: 2082 Rating: (931)
|
Hi Heisenberg, Thx for the attention... I've been working lately with EMT/EPHT's and in order to synchronize them manually, you need XMLTRANSFER, but also needed when you use Plant Automation Accelerator (Import/Export XML files). Apparently the XMLTRANSFER replaces the Synchronize editor for Control Module Types. It's extended with EMT/EPHT/Commands/Status. For difference, see attachment. It can be reached the same way like the CMT synchronize editor. There are to many @#^%^$% buttons in PCS7 But in short, for using CMT's only, you do not need XMLTRANSFER but you can use the "build-in" editor in PCS7. AttachmentDifference.zip (91 Downloads) |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to3 thankful Users |