7/7/2021 11:47 AM | |
Joined: 9/23/2005 Last visit: 10/15/2024 Posts: 4756 Rating: (726) |
If you receive four bytes whose hexadecimal representation is as you showed, then you do not need to convert anything. https://www.binaryconvert.com/result_float.html?hexadecimal=43BB8000 The question is how you receive the bytes/how the data is stored on your PLC and how to tell it to treat it as a variable of type REAL. |
Regards, |
|