7/13/2011 10:28 AM | |
Joined: 4/19/2008 Last visit: 11/21/2024 Posts: 1525 Rating:
|
Hi Patil, You can't used the CP341 on the UR2 H Rack, You have to used the ET200M, IM153-2 INTERFACE REDUND.BUNDLE on next to this IM you can mount the CP341........ you have to used the Active Bus Module. hope you have got the solution ..... |
Last edited by: Ammy at: 7/13/2011 10:31 AMAmmy |
|
This contribution was helpful to
1 thankful Users |
7/13/2011 11:56 AM | |
Joined: 8/18/2009 Last visit: 6/6/2025 Posts: 557 Rating:
|
Dear Ammy, is it must to used the Active Bus Module for CP 341 with IM 153-2. |
Rajkiran Patil |
|
7/13/2011 12:32 PM | |
Joined: 5/28/2008 Last visit: 7/8/2025 Posts: 4520 Rating:
|
Hello, Yes. You have to use the active bus module for your case. You have a fault tollerent system, so you have two different buses. And so, you have to use two different IM153-2. One for each bus. If you ordered the Red bundle6ES7153-2AR03-0XA0as mentioned by Ammy, you will recieve two IM153-2 with one bus module IM/IM. In this case you will save some mony as the price of Red bundle is approxmitlly double price of IM153-2, So, you will save the price of bus module IM/IM in case of ordering it separitlly. And you have to use the ET200M rack with function insert/remove. For CP341, use Bus Unit6ES7195-7HB00-0XA0 Hope this helps.
|
Ayman Elotaify |
|
This contribution was helpful to
1 thankful Users |
Follow us on