Dear Osman Sir/All, I am having a doubt regarding CP 343-1 Lean part no 6GK7 343-1CX10-0XE0 V3.0. It has 2 x 10/100 Mbps (IE SWITCH); RJ-45 ports . I want to know can I make it as a Profinet master to communicate with IM 153-4 HF and to send/receive from other Simatic station with CPU 314 and CP 343-1 Lean part no 6GK7 343-1CX00-0XE0 V1.0 or not ? Kindly help me in this regard. Appreciate your swift reply. Thanks and Regards ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 5/11/2016 11:57:13 AMNew subject after splitting |
|
5/11/2016 11:51 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054) |
hi Tanzeal, 6GK7 343-1CX10-0XE0 can not act as IO-Controller. But there are ways to communicate from 2 S7-300 with CP343-1lean. Have a look in this manual: CPU-CPU Communication with SIMATIC ControllersIn chapter 21.4.2 you can see all possible communication between two S7-300. Whit two CP343-1 lean you can use only open communication(OC) with the AG_SEND/AG_RCV. Here is a FAQ, that shows how to do it: How do you configure open IE communication via the integrated PN/IE interface of the CPU or via an Industrial Ethernet CP?hope this helps, regards, |