9/11/2013 4:54 PM | |
Joined: 1/21/2013 Last visit: 6/6/2024 Posts: 4620 Rating: (705) |
Hi Bosshard, Please note this forum is using the English language, translate your problem. |
9/12/2013 11:27 AM | |
Posts: 3 Rating: (0) |
Hello Daniel First thank you for your help. Attacheet you find the diagnostic from the CPU.Note:In the diagnose i think its evenement 10. So this problem is very particoulus.I never see this... I send back the CPU for repair..They testing for two days..no problem..We recoser the CPU in the machine and after 2 hours all LED's ware RED...again. After an alll over reset we reload the programm..the machine working well for vew houers and then...again STOP ... AttachmentCPU.zip (85 Downloads) |
9/12/2013 11:39 AM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (714)
|
Hello, I think the power supply is suspect nr1 or else the rack. I (google) have translated your Diag for others to review. Regards, Marcjan AttachmentDiagnostic_ buffer_en.zip (87 Downloads) |
Problem solved? |
|
This contribution was helpful to1 thankful Users |
9/13/2013 6:48 PM | |
Joined: 4/22/2010 Last visit: 5/3/2024 Posts: 5697 Rating: (714)
|
Hello and sorry, sorry because i did not read your post carefully If you have the same problem with multiple CPU, it can only be a problem in that type off CPU (should be known by Siemens by now) or there is a design fault in your system. I'm thinking about some serious EMC problems or unstable main power supply with short power drops. If all is installed by the rules i think you should go for a support request Regards, Marcjan |
Problem solved? |
|
Follow us on