3/5/2008 7:33 AM | |
Posts: 152 Rating: (2) |
Hi all cheers sunil Attachmentdetailerror.pdf (212 Downloads) |
3/5/2008 7:34 AM | |
Posts: 152 Rating: (2) |
error message
Attachmenterror.pdf (195 Downloads) |
3/5/2008 7:35 AM | |
Posts: 152 Rating: (2) |
compilation messsage
AttachmentcompileMsg.pdf (117 Downloads) |
3/5/2008 11:45 PM | |
Posts: 2661 Rating: (279) |
Try the following: 1. Overall reset the CPU, download the HWCONFIG and download the charts. 2. If still same error, check your setting for maximum communication jobs in CPU properties (see attachment). Increase this value and recompile and download. The help in the memory tab explains this setting in detail. AttachmentDokument1.pdf (234 Downloads) |
This contribution was helpful to2 thankful Users |
3/6/2008 6:57 AM | |
Posts: 152 Rating: (2) |
hi Phantom THANK YOU VERY MUCH. just reseting CPU solved my prob. I wonder. thank you. cheers sunil |
5/14/2012 10:39 AM | |
Posts: 1 Rating: (0) |
I have increased the Communication jobs to the maximum but the download error is still present i.e error linking blocks Fb5,FB10...... etc still occurs. |
5/17/2012 11:43 PM | |
Posts: 2661 Rating: (279)
|
Hi DominicN, Can you a screenshot of your error message? Regards |
Follow us on