Industry Online Support
Technical Forum
3/23/2009 10:02 AM | |
Posts: 7 Rating: (0) |
How many modules of DIGITAL IMPUT and DIGITAL OUTPOUT can i add to theCPU 226 mentioned on the above subject. |
Last edited by: kettaneh at: 3/23/2009 10:04 AM |
|
3/23/2009 10:10 AM | |||||||||||||||
Joined: 9/27/2006 Last visit: 10/9/2024 Posts: 12285 Rating: (2685) |
Hello kettaneh; From the A&D Mall:
|
||||||||||||||
3/24/2009 7:13 AM | |
Joined: 3/21/2006 Last visit: 10/7/2024 Posts: 10229 Rating: (1181) |
Hello Be careful, you must calculate your power budget to determine how much power (or current) the S7-200CPU can provide for your configuration. If theCPU power budget is exceeded, you may not be able to connect the maximum number of modules. See S7-200 manual (Appendix A for CPU and expansion module power requirements, and Appendix B to calculate your power budget). regards |
Follow us on