I read HSC count ID1000 in OB1 (100msec). HSC counting pulses only to 500Hz. Perhaps the reason is in the input filter 6,4msec or in configure? |
6/10/2015 12:20 AM | |
Joined: 7/7/2010 Last visit: 9/23/2024 Posts: 15217 Rating: (2417)
|
Yes, it is the input filter value. Set it to the smallest filter selection.
|
science guy |
|
6/10/2015 11:35 AM | |
Joined: 3/26/2009 Last visit: 8/22/2024 Posts: 138 Rating: (0) |
I will do it necessarily. [snip]
---------------------------------------------------------------------------------------------------- |