12/5/2016 4:05 PM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hello, when a HMI displays #### this means that the problem is in communication, which Profibus connectors uses, original Siemens? The minimum length of the cable is "1 meter" (but I have also used shorter and it works the same) Bus fault with Profibus communication - Entries - Forum - Industry ..., 7 and 15 mt is not a problem, maybe it is the reflection of the cable, terminators are okay? |
12/6/2016 7:49 AM | |
Joined: 8/9/2014 Last visit: 7/5/2024 Posts: 16 Rating: (0) |
Connector used are of Original Siemens.....And terminators on first and last connectors are OFF and the middle one is ON. |
12/6/2016 7:58 AM | |
Joined: 1/21/2013 Last visit: 9/4/2024 Posts: 4620 Rating: (707) |
Hello, Pay attention that the S7 200 is only SLAVE DP with EM277 What settings have to be made for a PROFIBUS DP connection ... but how the first and last are OFF, test first and last ON and OFF in the middle |
Last edited by: Ste39 at: 12/6/2016 8:59:18 AMEM 277 |
|
This contribution was helpful to2 thankful Users |