Hello, for positioning applicatoins with SIMATIC S7-1500 and SINAMICS S120 there are two possiblities: 1.) Using the technology objects inside the S7-1500 and make the programming by PLC Open blocks:
The X127 you can not use for that. You need a DP- interface on the SIMATIC, or use a CBE20 for CU320-2DP or you use a CU320-2PN. |
With best regards, |
|
7/15/2014 4:39 PM | |
Posts: 58 Rating: (0) |
OK i prefer the frist opcion 1.) Using the technology objects inside the S7-1500 and make the programming by PLC Open blocks: |
7/15/2014 5:28 PM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804) |
This is no problem for your configuration.
You can select in the Starter tool the Control Unit of the S120. In the expert list you can setup which interface (IF1 or IF2) should be using isochronous mode (parameter 8815). And with another parameter (p8839)you setup which communication is IF1 and or IF2. |
With best regards, |
|
4/14/2015 4:05 PM | |
Posts: 58 Rating: (0) |
Hi i need to download a document 68034568 but the web page in not available Do you know other way to download this document?
|
4/15/2015 11:09 AM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804)
|
Hello,
This document / link is still active: https://support.industry.siemens.com/cs/ww/en/view/68034568
|
With best regards, |
|
This contribution was helpful to1 thankful Users |