1/10/2015 12:18 AM | |
Posts: 153 Rating: (8) |
Is your encoder reversed? Sounds like a positive feedback condition. |
This contribution was helpful to1 thankful Users |
1/10/2015 10:19 AM | |
Joined: 11/21/2007 Last visit: 3/14/2024 Posts: 2323 Rating: (306) |
Thanks casajr This is a Motor with Drive Cliq. Encoder so I don't understand how the connections can be reversed ? Cheers Navnag |
There is no such thing as the last bug in a program |
|
1/12/2015 6:53 AM | |
Joined: 11/21/2007 Last visit: 3/14/2024 Posts: 2323 Rating: (306) |
Thanks pigroplc Customer had used a normal cable instead of Motion Connect which probably had the phases reversed. The problem was solved when we replaced the cable with a standard Motion Connect Cable the problem was solved. Cheers Navnag |
There is no such thing as the last bug in a program |
|
This contribution was helpful to1 thankful Users |
Follow us on