Hello the Basic Panels do not have a scripting ability, so you cannot create timestamps in the Basic Panel.so the correct solution is to use the PLc for that. (If you had a Comfort Panel then you could get it run in Panel) To synchroise the PLC and the HMI here some additional Information: https://support.industry.siemens.com/cs/ww/en/view/69864408 Bye Murof |