Hello The DB values are retained even if CPU goes to stop Mode. There are no direct methods to initialising a DB to its Default values. Please have a look at this nice post from Our friend IBN-Service for a method that you can use : Initialisation of DB by using the SFC83 Another Method ( Not so elegant ) is ti have another DB with Default values, whose values are never changed. You can copy this DB to your working DB in CPU startup program ( OB 100 ) using SFC20 ( Block Move ) Hope this helps Cheers Navnag |