2/18/2008 7:10 AM | |
Posts: 2348 Rating:
|
You can useSFC51/SFC13toreadoutDP-slavesstatesinOB100-thenyouwouldknowwhichslavesaremissing. SFC13 provides more info then SFC51, but is much slower. |
2/19/2008 4:25 PM | |
Joined: 9/23/2005 Last visit: 6/7/2023 Posts: 4184 Rating:
|
Hi, more two suggestions: 1 - Use the FC 125 (http://support.automation.siemens.com/BR/view/en/387257). It manage a DB, where each bit represents a slave status. 2 - Use Report System Error (http://support.automation.siemens.com/BR/view/en/5416665), if you just need to send the information to a HMI/SCADA. |
Denilson Pegaia |
|
2/20/2008 3:21 PM | |
Posts: 2348 Rating:
|
FC125 calls SFC51 inside:^) |