2/18/2008 7:10 AM | |
Posts: 2348 Rating: (264) |
You can useSFC51/SFC13toreadoutDP-slavesstatesinOB100-thenyouwouldknowwhichslavesaremissing. SFC13 provides more info then SFC51, but is much slower. |
2/19/2008 4:25 PM | |
Joined: 9/23/2005 Last visit: 10/18/2024 Posts: 4350 Rating: (1448) |
Hi, more two suggestions: 1 - Use the FC 125 (http://support.automation.siemens.com/BR/view/en/387257). It manage a DB, where each bit represents a slave status. 2 - Use Report System Error (http://support.automation.siemens.com/BR/view/en/5416665), if you just need to send the information to a HMI/SCADA. |
Denilson Pegaia |
|
2/20/2008 3:21 PM | |
Posts: 2348 Rating: (264) |
FC125 calls SFC51 inside:^) |