Hello bfg64, Here the link for Manual (inclusive Namur): http://support.automation.siemens.com/WW/view/en/19026151 On Top of Page 107you find awireing examplefor NO-Contacts (picture on the right) Suitable Sensors for Namur are: – In accordance with DIN 19234 and NAMUR (with diagnostic evaluation) – connected mechanical contacts (with diagnostic evaluation) This looks not so complicated. That’s the only way out. Other F-modules can’t handle wire break with NO-contacts. I have not other ideas. james |
1/27/2012 10:43 AM | |
Posts: 5 Rating: (0) |
Thank you for this information. Bye Bye |