1/20/2022 10:05 AM | |
Joined: 5/3/2017 Last visit: 5/25/2022 Posts: 569 Rating:
|
Hi EBM101, SIMATIC BATCH is a standard application of PCS 7. And it controls the plant from a higher level (the recipe system) and it generate always an report. The controlling of the AS is done via SFC-types. PCS 7 SIMATIC BATCH V9.0 Getting Started PM-CONTROL is also a recipe system, but for servals WinCC Versions, not only for PCS 7. And the AS is controlled via WinCC tags. Also you have no reporting system (the reporting is available with PM QUALITY). And a Getting Started with PM-CONTROL is available, please contact WinCCAddon.Automation@siemens.com With regards |
This contribution was helpful to
1 thankful Users |
1/22/2022 9:59 AM | |
Joined: 7/3/2014 Last visit: 5/11/2022 Posts: 6 Rating:
|
you can also use the APF library https://support.industry.siemens.com/cs/es/en/view/109740513 Best regards jc |
Last edited by: arcos vivar at: 01/22/2022 10:00:21Last edited by: arcos vivar at: 01/22/2022 10:01:17Last edited by: Jen_Moderator at: 01/24/2022 11:39:55Optimized link. |
|
This contribution was helpful to
1 thankful Users |