The digital output can be operated by status word 1, for example. In the manual 'Operating Instructions', in the 'parameter list', find Status Word 1. Here, r0052:0 to r0052:15 is listed. The number after the : (colon) defines which bit of status word one is to operate the digital output. Example: status word 1 r0052:00, inverter ready, (the 52.0 is the number to enter into P0731:0 = 52.0) r0052:01, inverter ready to run r0052:02, inverter running r0052:03, inverter fault active Also: for Status word 2 r0053:00, DC brake active r0053:01, Frequency above P2167 r0053:00,Frequency above P1080 You need a copy of the V20 manual to see the above options. Also if you can find a useful 'digital' high signal in the parameter list, you can use it to activate either of the digital outputs. The V20 is referred to as a 'basic inverter' in the SIEMENS web site, but there are a great number of things available in this inverter, but you have to find them which can be difficult. Come back if I can help further. Tractor |