Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054)
|
hi, Which PLC do you have exactly? regards, |
FCK WAR! |
|
2/28/2022 9:25 AM | |
Joined: 3/11/2019 Last visit: 9/6/2024 Posts: 1569 Rating: (289) |
Hi, do you use a software controller, or a regular S7-1500 cpu? A S7-1500 does not have USB, so there is no need to deactivate. But a S7-1500 need a SIMATIC Memory Card to operate, otherwise it can not be used. So there is no option die deactivate the Slot for the SMC. But the slot can be locked with a padlock. Protection by locking the CPU/interface module
regards sancruz |