6/3/2014 9:32 PM | |
Joined: 3/14/2008 Last visit: 8/10/2024 Posts: 2082 Rating: (931) |
Well....... You both are right First, you cannot interconnect two outputs to one input. Never will be done Second, you can create however multiple"virtual" interconnections to one input. For this, you need to set the option: optional in the control module type For example: I have a FB open driver block and a FB close driver block. Both blocks are dragged into the "Technological I/O" on top. Youselect the QBADparameter fromFBopen and drag it under FB openblock.Samegoes for the other. Next you select the parameter which you want connect multiple interconnections to and put the parameter also in the technological IO list, lets say: PROTECT Now you will drag the QBAD parameter to the PROTECT parameter and a interconnection is made.You will also do that for the other QBAD. Now you can see multiple interconnections connected to the PERMIT. However, inorder to use this, you will need to create variants of control modul types in the AdvES editor.A nice example is a motor with an interlock2 and interlock8 block connected to INTLOCK. You can make two variants, without changing or creating a new control module type. |
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to2 thankful Users |
Follow us on