2/15/2018 1:17 PM | |
Joined: 10/11/2006 Last visit: 7/23/2024 Posts: 5877 Rating:
|
Hello, use the systemvariables of the following object for diagnose. synchronizingState syncstate state currentslavedata currentSyncPosition currentmasterdata Further info: 2.2.5 Synchronization https://support.industry.siemens.com/cs/ww/en/view/109749950 |
With best regards, |
|
2/20/2018 9:19 AM | |
Joined: 10/11/2006 Last visit: 7/23/2024 Posts: 5877 Rating:
|
Hello, it is possible to synchronize via distance, then the distance must be big enough. 2.2.5.4 Synchronization via a specifiable master value distance The path length of the master value is specified in the parameter syncLength. As a result, synchronism is always achieved in the setpoint specification. The dynamic response during synchronization is dependent on the calculated profile via the master value and on the change in the master value. The dynamic response values specified in the command are not active. Via dynamic: 2.2.5.5 Synchronization profile When this synchronization profile is used, a synchronization profile is calculated according to the specified dynamic response parameters and the master value dynamic response that exists at the start of the profile. The profile is appliedaccording to the master valuefor leading synchronization andaccording to timefor trailing synchronization. Check direction 2.2.5.2 Synchronization direction You can use the MCC- Command. This command show all necessary settings. It is possible to export a MCC-Chart as ST (Structure Text). Then you can import as ST. 6.7.6 Cam On https://support.industry.siemens.com/cs/ww/en/view/109749951 Check your alarms. |
With best regards, |
|
Follow us on