10/7/2014 2:57 PM | |
Posts: 1368 Rating: (126) |
Hello, do you know this FAQ? Perhaps it helps you http://support.automation.siemens.com/WW/view/de/21848242 Which CPU, TIA Versiondo you use? |
10/7/2014 6:58 PM | |
Joined: 1/28/2009 Last visit: 9/10/2024 Posts: 6849 Rating: (1365) |
Hello, Just to provide another suggestsion to test,If you are developing your codes in OBs or any functions (blocks), simply define an ANY parameter in temp area and fill the data based on the structure explained in STEP 7 online manual.Declare the ANY parameter as IN/OUT parameters for SFC15/SFC14.I think this is less ambigous for the controller.
I hope this helps, Hamid Hosseini Attachment1.zip (798 Downloads) |
10/8/2014 8:42 AM | |
Posts: 112 Rating: (2) |
DEARhdhosseini JUST READ THE (PIWXXX) ADDRESS IN VAT TABLE AND CHECK THE DATA IS READING OR NOT THEN U CAN GO FOR (SFC14/15)........ IF U ANE NOT RECEVING ANY DATA THEN CHECK (SFC14/15)...IF NOT THEN CHECK FROM CLIENT SIDE DATA SEND & GSDS FILES CONFIGURED ...................... ...TO SOLVE O ISSUE
|
Last edited by: GOWDA at: 10/8/2014 8:44 AM |
|
8/6/2015 10:27 AM | |
Posts: 1 Rating: (0) |
This answer is OK. Check the number of bytes are you receiving and set the buffer in SFC 14/15 to this length |
2/21/2023 11:36 AM | |
Joined: 1/8/2019 Last visit: 3/5/2024 Posts: 1 Rating: (0) |
It works!! Thank you! |
Follow us on