10/31/2016 9:29 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1054) |
hi,
is there anything loaded on the CPU? you need to load a valid HW-configuration and a program to the CPU. regards, |
FCK WAR! |
|
10/31/2016 9:33 AM | |
Joined: 5/12/2006 Last visit: 9/20/2024 Posts: 22365 Rating: (3011) |
Hi, HW Config should be loaded because the Opton handling is enabled, this is only possible with a loaded HWConfig. But if this Option is active you need a program in the startup to activate a valid data set for Option handling. If you need no option handling deactivate the option in the PLC Porperties and download the Project to the plc.
Christoph |
This contribution was helpful to4 thankful Users |
6/28/2021 8:11 AM | |
Joined: 10/22/2013 Last visit: 9/4/2024 Posts: 8 Rating: (4) |
In PLC properties/Configuration control, the tick mark in "Allow to reconfigure the device via the user program" must be removed. |
This contribution was helpful to8 thankful Users |
1/20/2022 5:15 PM | |
Joined: 3/19/2020 Last visit: 3/13/2023 Posts: 1 Rating: (0) |
Thank you |
2/16/2023 4:50 AM | |
Joined: 12/28/2022 Last visit: 1/20/2024 Posts: 2 Rating: (0) |
Thank you so much!!! |
6/18/2024 10:11 AM | |
Joined: 4/28/2015 Last visit: 9/10/2024 Posts: 1 Rating: (0) |
thanks |