1/12/2013 1:14 AM | |
Joined: 4/18/2012 Last visit: 7/9/2024 Posts: 41 Rating:
|
Hi, Good day to you. I need some help on the following situations: I have designed a monitoring project system, which is a computer engineer and four operator stations,With the following characteristics. Was configured as two server computers, two client stations and a computer station engineering. Software : STEP7 5.4+WINCC 7.0 SP2 Hardware:S7400H Given the above information of the system has three major problems: 1-After making changes in the engineering station is not able to load the other stationsin the runtime is the software WINCC. The software WINCC station should be closed, so then this should be done. 2-Station server is configured, but the server station is out of service, the previous data (Alarm+...) will not be replaced on the standby server?In fact, they seem to be server stations should not sync together. 3-You are correct in terms of the design of monitoring systems, capable of operation the engineering station.(Runtime+Configuration) thanks for you ,if you provide any information and documents. Besst Regards, Saeed AttachmentPRJ_900508_R.pdf (466 Downloads) |