3/24/2020 11:18 AM | |
Joined: 2/20/2018 Last visit: 9/13/2024 Posts: 30 Rating: (3) |
Hello Dear Colleagues, We need to choose an external encoder for a press application. We have 1500T CPU + ET200SP + S120 in our configuration. We have two options for an encoder: 6FX2001-5FN25
or 6FX2001-5FD25-1AA0 I know that there is a difference of resolution between two products. Apart from that, what should we consider when deciding between two encoders? If we use profinet encoder we will read the data directly with IRT, if we use drive cliq encoder CU 320-2 PN will read the data from DriveCliq and we will read that data from CU 320-2 PN with IRT, do you think that would make a difference? Best regards and thank you for your support. |
Last edited by: OnderYalcin at: 03/24/2020 11:21:12 |
|
3/24/2020 1:44 PM | |
Joined: 7/7/2010 Last visit: 9/20/2024 Posts: 15213 Rating: (2417) |
Having a drive-cliq encoder let's the drive close the control / feedback loop and just report to the PLC when it's done or in position rather than relying on the plc to handle that. It is well worth it to have a drive cliq encoder if your system supports it.
|
science guy |
|
This contribution was helpful to1 thankful Users |
3/24/2020 2:01 PM | |
Joined: 1/4/2013 Last visit: 9/21/2024 Posts: 1126 Rating: (102) |
Absolutely correct |
Searching for Siemens used/new equipments ? |
|
3/24/2020 4:09 PM | |
Joined: 2/20/2018 Last visit: 9/13/2024 Posts: 30 Rating: (3) |
I think I should have mentioned that, the drive will have its own encoder as a feedback. The external encoder will be used as a master for another drive.
|
Follow us on