Industry Online Support
Technical Forum
10/8/2011 4:24 AM | |
Posts: 50 Rating: (0) |
Hi, I have a 6SN1123-1AA00-0GA0 that is giving me an alarm F09. Can some one tell me which manual covers this unit. Thanks |
10/8/2011 7:14 AM | |
Posts: 2964 Rating: (478) |
Hello..... What control is this? i think this is connected with Simodrive 611A with Spindle control card 6SN1121 series check this link for more informations.... https://www.automation.siemens.com/doconweb/content.asp?item=12807&cd=sinumerik_simodrive_04_2010_e&scope=all F09 alarm means : Fault Encoder system ( Motor Encoder) cause: Motor encoder not connected or defective Motor encoder cable defective Measuring circuit 1 (speed actual value sensing) defective, not correctly inserted or incorrectly equipped(P–150).The fault message can be suppressed via P –090 bit 1 from FW 2.00 onwardsRemoving the fault: Check the encoder cable/shielding, or Replace the motor encoder, or Replace the control board |
Follow us on