11/16/2018 9:56 PM | |
Joined: 3/14/2008 Last visit: 7/11/2024 Posts: 2075 Rating:
|
Hi, you have a problem with the group display as well in the top left corner. Please do an AS compile change and OS compile to check if this solves the problem. If not, try inserting a copy of the SFC and check if that one works.. |
If I could help you, you can use the RATE button. Thank you. |
|
11/16/2018 11:02 PM | |
Joined: 3/14/2008 Last visit: 7/11/2024 Posts: 2075 Rating:
|
Hi matt1115, OK, I think you are using a SFC type/instance? As default, the Restart button is NOT visible for types/instances...See the attachment. You can enable the Restart button in the faceplate of the sfc. Note that this is the faceplate for types/instances, but you also have this faceplate for charts-> @pg_@sfc_rts_head.pdl. Enable the button, save the faceplate and Exit runtime and restart WinCC runtime and check again. Also note the SFC assignments: Restart in the "Held / Held (Error)" state ENSTART = 1 and ENRESTART = 1 must be set to be able to restart in the "Held / Held (Error)" state. You can find additional information about multiple simultaneously pending commands in the sections:
|
If I could help you, you can use the RATE button. Thank you. |
|
This contribution was helpful to
1 thankful Users |
11/16/2018 11:30 PM | |
Posts: 23 Rating:
|
Thank you! Very helpful! |
11/19/2018 11:29 AM | |
Joined: 3/14/2008 Last visit: 7/11/2024 Posts: 2075 Rating:
|
Great! Good luck |
If I could help you, you can use the RATE button. Thank you. |
|
Follow us on