2/27/2011 1:04 PM | |
Joined: 1/28/2009 Last visit: 6/26/2024 Posts: 6841 Rating: (1360) |
Dear Tomy Master You can find description of these functions(FB 58 "TCONT_CP" and FB59 "TCONT_S") in this link: PID Temperature Control In chapter 6(Examples for the Temperature Controllers),Their applications with a process simulator function combined.So, it would be helpful to follow the examples and learn how to use and parameterize the functions.The examples are available as "sample project zEn01_13_STEP7__PID-Temp" and can be accessed easily in SIMATIC Manager (File->open->sample projects). Some FAQ on this topic: 1-What should you pay attention to when presetting the setpoint value for controller optimization on FB58 TCONT_CP? 2-What should you pay attention to with feedforward control on control block FB58 "TCONT_CP"? 3-How do you estimate the sampling interval CYCLE and the largest possible number of controllers in a S7 CPU? 4-How can I optimize PID Temperature Control using STEP 7 V5.3 SP2? 5-System deviation despite setpoint value = actual value parameterization BR |
Last edited by: hdhosseini at: 2/27/2011 1:13 PM//FAQ added |
|
3/7/2011 10:08 AM | |
Joined: 3/21/2006 Last visit: 4/25/2024 Posts: 10228 Rating: (1181) |
Check it.
AttachmentZen01_13.zip (1469 Downloads) |
This contribution was helpful to1 thankful Users |
3/7/2011 11:44 AM | |
Joined: 1/28/2009 Last visit: 6/26/2024 Posts: 6841 Rating: (1360) |
Dear Tomy Master Also check this attachment for changing the default parameters with VAT. Progran in continuous controller folder of "sample project zEn01_13_STEP7__PID-Temp" is initialize the PID controller to manual.We turn done by reseting DB58.DBX42.1.Then PID algorithm automatically reacts to changes in setpoint .Note, as it shown in the attachment, increasing GAIN(DB58.DBD166) can cause overshoot but icreasing the Ti (DB58.DBD170) decreases steady state error.TD (DB58.DBD174) is zero to eliminate effect of D controller.As TM_LAG is part of differentiator ,it has no effect in this case. BR AttachmentFB58_PARAMETERIZE.zip (1924 Downloads) |
Last edited by: hdhosseini at: 3/7/2011 11:45 AMLast edited by: hdhosseini at: 05/18/2019 23:09:47 |
|
This contribution was helpful to1 thankful Users |
Follow us on