4/4/2018 2:32 PM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804)
|
Hello, the following error is defined as follows: following error [LU] = position setpoint [LU] - position actual value [LU] LU = length unit The following error can be eliminated by optimization of the drive. (Position, speed and current controller.) There is an optimization guideline for this available: https://support.industry.siemens.com/cs/de/en/view/60593549 A big improvement, if you use SINAMICS FW 4.8 or more recent, is to activate the speed pre control p2534 = 100 %. Then the following error is zero during constant velocity. If you want to decrease the following error during acceleration / braking you need to set up the torque pre control also. |
With best regards, |
|
4/6/2018 10:24 AM | |
Joined: 10/11/2006 Last visit: 9/18/2024 Posts: 5906 Rating: (804)
|
Hello, it looks like there is something wrong in your project. I suggest to create a Support request and attach the project and a trace of r2665 r2666 r2561 r2521 r2565 r2524 r898 r899 https://support.industry.siemens.com/my/ww/en/requests/#createRequest |
With best regards, |
|
This contribution was helpful to1 thankful Users |
Follow us on