Hi, you can access those parameters by acyclic reading/writing commands from the PLC. Therefore there are ready to use FBs available. Check out the SINA_PARA FB from the drive lib. Either you find it in the Global libraries of your TIA Portal already or you can download it from here: https://support.industry.siemens.com/cs/ww/en/view/109475044 To the second problem: I do not really understand that. As you want to access p1001 I think you are working with fixed speed setpoints (at least for one command data set). In case you have saved your drive parameterization retentively (copy Ram to Rom) this value should not change after Power Off/On. What do you do when switching to another CDS? Where comes the setpoint from in this case? And what exactly is the problem then? |