9/11/2018 5:33 PM | |
Joined: 7/7/2010 Last visit: 9/24/2024 Posts: 15222 Rating: (2417)
|
X2-Terminals 3 & 4 wires should be connected to 2 digital inputs is my best guess after reading the documentation : https://cache.industry.siemens.com/dl/files/799/109737799/att_884200/v1/gps2000_en_2016-01_V10_a.pdf If you have it powered up, can you monitor the signals on X2-3 & 4 to see they are simply inverted? Did you already install the FB from the CD to your PLC project? The inputs to that FB should help. For example, if it only references a single digital input, then you only need to connect one of them. The only other problem is to ensure 24V common for the PLC input and the DCF77 0V reference are the same (power supplies 0V terminal bonded to same potential).
Attachmentgps2000_en_2016-01_V10_a.pdf (54 Downloads) |
Last edited by: Jen_Moderator at: 9/12/2018 10:29:01 AMAdded file as an attachment. science guy |
|