9/14/2021 5:24 PM | |
Joined: 9/27/2006 Last visit: 4/27/2024 Posts: 12257 Rating: (2665)
|
Hello Grixo; The screenshot you have presents a multidrop configuration with HART instruments. The Siemens HART modules only support monodrop connections, each HART instrument is connected to a separate channel on the HART modules. https://support.industry.siemens.com/cs/ww/en/view/22063748/20140822027 Hope this helps, Daniel Chartier |
This contribution was helpful to2 thankful Users |
9/15/2021 8:59 AM | |
Joined: 1/18/2019 Last visit: 12/1/2023 Posts: 82 Rating: (3) |
Thanks really helpful information. I think each channel should have own ID for HART but at TIA V15.1 I can not see that option. Am I doing something wrong? AI card is 6AG1331-7TF01-7AB0 and CPU 317-2PN/DP
|