8/7/2015 2:31 PM | |
Joined: 12/18/2014 Last visit: 7/27/2024 Posts: 33421 Rating:
|
The logo can only read 0-10 V. If you want to read a pressure sensor, which outputs a voltage signal of 0-5V at 0-1 bar, then you need to cheat. 0-5 V = 0-1 bar Then you must parameterize the analog input as if you had a sensor that outputs 0-10V for a range of 0-2 bar. 0-10 V = 0 - 1000 units = 0-2 bar. Then with an arithmetic unit customize the units of the measurement range. To obtain a resolution 0.002 bar per unit. Attachmentpressure.zip (521 Downloads) |
8/7/2015 3:12 PM | |
Joined: 12/18/2014 Last visit: 7/27/2024 Posts: 33421 Rating:
|
And here is the complete solution. With the setting values of pump and solenoid you have to try.
Attachmentpressure_V2.zip (569 Downloads) |
This contribution was helpful to
2 thankful Users |
8/10/2015 11:52 AM | |
Joined: 12/18/2014 Last visit: 7/27/2024 Posts: 33421 Rating:
|
Which Logo have you? 0BA8? Or other? |
8/10/2015 12:52 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4770 Rating:
|
|
8/10/2015 2:01 PM | |
Joined: 4/28/2015 Last visit: 3/15/2024 Posts: 26 Rating:
|
I have 0BA8 - Logo! 12/24 RCEo variant. Andrew
|