4/12/2017 9:35 AM | |
Joined: 4/24/2006 Last visit: 8/9/2024 Posts: 8713 Rating:
|
Hello Abul Adnan, It looks like you got some alarms on your HMI Panel. Please have a look at the following link: SIMATIC HMI WinCC flexible 2008 Communication Part 1 See Appendix (9.1) for more information about System Alarms. Best regards, Wizard |
This contribution was helpful to
1 thankful Users |
4/13/2017 2:51 PM | |
Joined: 4/24/2006 Last visit: 8/9/2024 Posts: 8713 Rating:
|
Hello Abul Adnan, I guess it worked for a long time? Could it be, someone did try to change a value. And the value that was entered was too high? So it is discarded by PLC. Best regards, Wizard |
4/13/2017 3:10 PM | |
Joined: 6/11/2013 Last visit: 1/1/2024 Posts: 6 Rating:
|
But why it is recurring on the display screen during the operation/process ? |
4/13/2017 3:59 PM | |
Joined: 4/24/2006 Last visit: 8/9/2024 Posts: 8713 Rating:
|
Hello, So, these messages are coming back everytime? Since when does this happen? Did something change in plc or hmi? Best regards, Wizard |
4/13/2017 4:57 PM | |
Joined: 6/11/2013 Last visit: 1/1/2024 Posts: 6 Rating:
|
Nothing has been changed except the re-commissioning of OP-277 with the old backup program which was done in January 2016 and since then it was running perfectly. These errors recurred during the previous week. Regards. |
4/14/2017 8:39 AM | |
Joined: 4/24/2006 Last visit: 8/9/2024 Posts: 8713 Rating:
|
Hello, Do you use any scripting in your project? Perhaps you can check in your project where the tag DB11DW22 is used. Best regards, Wizard |
4/17/2017 10:20 AM | |
Joined: 6/11/2013 Last visit: 1/1/2024 Posts: 6 Rating:
|
I will check the tag and will update. Thanks. |