Industry Online Support
Technical Forum
10/25/2014 9:29 PM | |
Posts: 2 Rating:
|
Hi, I am a bit of a novice and would really appreciate some guidance on how best to control a timed sequence. Basically its a pump and solenoids, the motor runs for 1 hour then changes to the next solenoid and runs for another hour, has for pause for an hour then does the final solenoid. The next sequence needs to be triggered by the end of the previous sequence, it just runs in a big loop. I have attched an outline of what I want to do. What is the best way to do this? Many thanks GT AttachmentBatch plant.zip (283 Downloads) |
10/26/2014 9:22 AM | |
Joined: 12/27/2006 Last visit: 8/18/2024 Posts: 1197 Rating:
|
I have make something for you. You can make changes toit, its only the basic of your wishes. And you must set the timers to the correct time, now its for simultion, I have no patient to wait 4 hours to see if the programm works correctly. Attachmentvolgorde.zip (346 Downloads) |
This contribution was helpful to
1 thankful Users |
10/26/2014 9:48 AM | |
Posts: 2 Rating:
|
That is brilliant, just what I was looking for. Very simple. Thanks for your time, really appreciate your help Cheers |