Hello! I also have a question related to the subject. How can I detect if the STO function is active on V90 drive? Are there status bits for the OFF(1..3) state that the drive can be in? I would like to use the fact that the STO function is active further in my program to light up a signaling lamp to show the fact that the door is open. My safety components consist of a magnetically-operated safety switch and a safety stop push button. ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 09/29/2021 13:19:51New subject after splitting |
|
9/30/2021 4:07 PM | |
Joined: 10/11/2006 Last visit: 12/20/2024 Posts: 5974 Rating: (820)
|
Hello, the V90 has no safe output signal, so the signal won`t be a safe signal, you just use a standard digital output to indicate the STO status. Check out chapter 4.3.1.2 of the V90 operating instruction manual for more info https://support.industry.siemens.com/cs/ww/en/view/109793501 |