Hello Mike; If you are using the DP/PA coupler to connect a Profibus-PA instrument directlyto a Profibus-DP network (working at 45,45 kB) then you do not need to insert it in the DP configuration of the Profibus-DP master. This is valid on any Siemens CPU or programming software that supports Profibus-DP configurations. See this extract from the followingSiemens FAQ, and look at the example of a configuration of a PA slave on a DP/PA coupler you will find there: How do you set up the DP/PA link and how do you configure the DP/PA link and DP/PA coupler? The DP/PA coupler can be operated in standalone mode. In this case, the DP/PA coupler is not configured in the Hardware Configuration. The PROFIBUS PA field devices are configured directly on the PROFIBUS DP master system of the CPU. Hope this helps, Daniel Chartier |