10/30/2014 3:45 PM | |
Joined: 9/27/2006 Last visit: 9/25/2024 Posts: 12283 Rating: (2685) |
Hello Mike; If you are using the DP/PA coupler to connect a Profibus-PA instrument directlyto a Profibus-DP network (working at 45,45 kB) then you do not need to insert it in the DP configuration of the Profibus-DP master. This is valid on any Siemens CPU or programming software that supports Profibus-DP configurations. See this extract from the followingSiemens FAQ, and look at the example of a configuration of a PA slave on a DP/PA coupler you will find there: How do you set up the DP/PA link and how do you configure the DP/PA link and DP/PA coupler? The DP/PA coupler can be operated in standalone mode. In this case, the DP/PA coupler is not configured in the Hardware Configuration. The PROFIBUS PA field devices are configured directly on the PROFIBUS DP master system of the CPU. Hope this helps, Daniel Chartier |
Last edited by: dchartier at: 10/30/2014 3:46 PM |
|
This contribution was helpful to1 thankful Users |
4/1/2015 3:37 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4767 Rating: (123) |
|