1/12/2010 12:29 AM | |
Joined: 7/2/2008 Last visit: 9/30/2024 Posts: 928 Rating: (309) |
Hello TEBANCH, Hello Ayman, I'm afraid Imay disagree with what you have said this time. By looking at this FAQ you will find that max. number of AS-i masters in central rack depends on current capacity of backplane bus. Siemens recommends 3 to 4 AS-i masters in central rack. The point is that you are limited to max. of 1.2A in backplane bus for all CPUs (except 312-IFM) and the CP343-2 consumes a max. of 200 mA at 5VDC (Backplane bus) which means that theoretically you are limited to 6 per rack but it's recommended to limit yourself to 3or 4 AS-i masters per rack. For more info. check chapter 5.4 in S7-300 Automation System, Hardware and Installation: CPU 312IFM - 318-2 DP
Unfortunatelythe HW compilerwill always failto detect configuration mistakes related to current consumption calculations. Best regards. H-H |