10/22/2016 7:04 PM | |
Joined: 7/28/2015 Last visit: 3/21/2024 Posts: 72 Rating: (1) |
With one Logo8 FS4 as master, how many Logo8 FS4 as Modbus can be connected? With KN700 Basic panel is possible have only 4 connection, this mean 4 Logo8 as master. What can be the maximun Logo! number configuration? ------------------------------------------------------------------------------------------ |
Last edited by: Min_Moderator at: 10/24/2016 11:27:14 AMNew subject after splitting |
|
10/22/2016 7:13 PM | |
Joined: 12/18/2014 Last visit: 11/9/2024 Posts: 34177 Rating: (4256)
|
Nothing has changed. Also the FS4 can not have more than 16 connections, a maximum of 8 dynamic and a maximum of 8 static. A LOGO! FS4 can also only connect to one HMI. The difference is only that the FS4 also mastered MODBUS. AttachmentLOGO! 8 Soft manual 0BA8 2016_07 (FS4) pages 29-31.pdf (549 Downloads) |