12/23/2020 5:11 AM | |
Joined: 1/17/2013 Last visit: 11/9/2024 Posts: 1106 Rating: (7) |
Dear Experts, I try to do but it has error as picture. How can I fix it ? Best Regards, Vorapob |
Best Regards, |
|
12/23/2020 3:28 PM | |
Joined: 1/17/2013 Last visit: 11/9/2024 Posts: 1106 Rating: (7) |
Dear Experts, Why I can't setting Isochronous mode with SIMOTION D452-2DP/PN ? |
Best Regards, |
|
12/28/2020 11:15 AM | |
Joined: 10/11/2006 Last visit: 11/8/2024 Posts: 5935 Rating: (815)
|
Hello, minimal IRT cycle for V90 is 2ms. With Simotion TO (e.g Posaxis) and V90 only GSD is released. https://support.industry.siemens.com/cs/ww/en/view/109737269 |
With best regards, |
|
12/28/2020 11:50 AM | |
Joined: 1/17/2013 Last visit: 11/9/2024 Posts: 1106 Rating: (7) |
Dear Technology Team, Thank you for your information. Do you have step by step to do with Simotion TO (e.g Posaxis) of V90 ? I would like to do in my project please. Best Regards, Vorapob |
Best Regards, |
|
1/4/2021 2:06 PM | |
Joined: 10/11/2006 Last visit: 11/8/2024 Posts: 5935 Rating: (815)
|
Hello, it is similar to chapter 4.2 of S210 example. Servo_fast is not necessary and telegram 102 is possible. Configuring technology objects with SIMOTION SCOUT TIA and SINAMICS S210 https://support.industry.siemens.com/cs/ww/en/view/109759892 |
With best regards, |
|
This contribution was helpful to1 thankful Users |
1/5/2021 7:51 AM | |
Joined: 1/17/2013 Last visit: 11/9/2024 Posts: 1106 Rating: (7) |
Dear Technology Team, Thank you very much for your helping. Best Regards, Vorapob |
Best Regards, |
|
1/5/2021 9:16 AM | |
Joined: 1/17/2013 Last visit: 11/9/2024 Posts: 1106 Rating: (7) |
Dear Technology Team, I read at the page 21 and follow it but it don't have "Use Servo_Fast" to select. I don't know why? In manual it use D435-2 DP/PN but I use D325-2 DP/PN. How can I select Real Time Setting > Send clock ? Best Regards, Vorapob |
Best Regards, |
|