4/14/2014 7:48 PM | |
Posts: 11 Rating:
|
Project Screebshot |
4/14/2014 7:49 PM | |
Posts: 11 Rating:
|
Error |
4/14/2014 8:37 PM | |
Joined: 11/21/2007 Last visit: 7/7/2024 Posts: 2325 Rating:
|
Hello Emz There are upto Three types of Startup OBs available in S5 and S7 ( Depending on the type of CPU ). In SIMATIC-S5 : OB 20 - Manual or Automatic Cold Restart OB 21 -Manual Warm Restart OB 22 - Automatic Warm Restart after Power Failure In SIMATIC-S7 : OB 100 - Warm Restart OB 101 -Hot Restart ( Not in S7-300 and S7-400H ) OB 102 - Cold Restart In S7 300 CPUs only Warm Restart ( OB 100 ) is possible ( Excepy CPU318 / 319 ) Normally OB 21 of S5 should be converted to OB 100 of S7. and OB 20 should be converted OB 102 ( If available in S7 CPU ) Of the CPu selected by you does not support the Startup OB type ( e.g. Cold Restart ) then it cannot be used. You can however evaluate the type of Restart inside the Startup OB Local Data ( Pl see attachment ) Hope this helps Cheers Navnag AttachmentS7_300_Startup_OBs.pdf (398 Downloads) |
There is no such thing as the last bug in a program |
|