9/24/2019 10:12 AM | |
Joined: 11/2/2015 Last visit: 10/16/2021 Posts: 39 Rating: (0) |
Dear All ! Thank for suggest. How to creat CDS ? Please help me manual about it Thank |
2/20/2021 1:28 PM | |
Joined: 9/6/2008 Last visit: 5/7/2022 Posts: 1121 Rating: (86) |
Hi Just finished a project with G120C about 50 number connected on Profinet MRP with S71500 PLC. Was searching on for CDS selection from PLC mode without hardware selector for Local/Remote. Just adding my part. My project is created with example of G120C Block that i have modified for HW_IO parameter in the block interface. See the attached library. TIA V16 Prof used. You can select the Bit 15, That i have changed in the block input as Local/Remote for CDS selection. All you have to do is following parameters additionally, P20081 - 1 (Select runtime Group) r20078 -r2090.15 (CDS selection Bit from PLC send word bit15), P810 - Change to r20079 (QNOT bit, as the PLC Profinet failure will change over the CDS to Local terminal Mode) Now with Bit 15 in the block- Remote=1, You can control the VFD on local remote. Please note: Default CDS 0 - is the field bus Setpoint. and the you need to Invert the bit coming from PLC. Hope this helps others,Keep sharing guys....... AttachmentG120C Block.zip (253 Downloads) |
Last edited by: Jen_Moderator at: 02/22/2021 10:35:46Optimized link. Jazz |
|