when i use siwarex MS FTC FTA ,how i to know the loadcell is damage? thank you |
Last edited by: weighting at: 4/15/2012 2:01 PM |
|
4/16/2012 9:17 AM | |
Posts: 80 Rating: (1) |
Most of load cell will give 10-15mV reading if we measure between +Input and -Input. Provided 10Vdc is feed at +Exc and -Exc. Azad
|
4/16/2012 10:06 AM | |
Posts: 206 Rating: (22) |
Hello wieghting, in chapter 8 of the load cell manual http://support.automation.siemens.com/WW/view/en/32466622 you can find instructions how to test a load cell. Regards ABenno |
4/17/2012 2:48 PM | |
Posts: 17 Rating: (0) |
thankyou for explain. If initialohm is 300,than one of the loadcell is damage,so the ohmchanged. thesiwarexmodelhave alarm? how can i chek the ohm? |