Hello, I would also recommend to use e.g. telegram 1 with SINA_SPEED FB from DriveLib. But if you really want to change p1001 you will need to set up an acyclic write command (as this parameter is not a connectable parameter and cannot be connected to the cyclic telegram). So you can use the SINA_PARA block from the DriveLib: https://support.industry.siemens.com/cs/ww/en/view/109475044 (and I would recommend also to check out the SINA_SPEED block for cyclic data exchange and continuously change of speed setpoint using telegram 1, this is the easiest solution!) |