2/27/2024 10:05 AM | |
Joined: 2/19/2015 Last visit: 4/26/2024 Posts: 11 Rating: (0) |
Hello everyone I've recently learned that instead of having the CPU going into STOP when there's a hardware issue like an input module having a fault or losing connection to an ET200SP, the CPU can be kept running by using the OB82 or OB86 blocks. If I'm going to do that, I'd like to do it correctly so the error in question can be displayed on the touch panel and maybe indicated with something like a lamp outside of the control cabinet. I've found this pdf from siemens, but it's nearly a decade old and I can't find the FB/FCs it mentions like FC2086 in neither the instructions register nor the library register. How is writing those OBs correctly done in TIA 17 for an S7-1500? Attachment98210758_User_defined_diagnostics_DOKU_v20_en.pdf (139 Downloads) |
Last edited by: The Helping Hand at: 02/28/2024 09:51:29File attached from link |
|
2/27/2024 10:14 AM | |
Joined: 7/9/2015 Last visit: 4/26/2024 Posts: 3814 Rating: (554)
|
Hi, please check this FAQ - it also contains a PDF from 2019 for you topic. Diagnostics in User Program with S7-1500Regards, Towome |
|
|
2/27/2024 1:12 PM | |
Joined: 2/19/2015 Last visit: 4/26/2024 Posts: 11 Rating: (0) |
Thanks for your answer, but I'm unable to open both
In both cases it tells me I need "G110M, G120, G120C, G120D, G120P" when I try to open them in either TIA 17 (newest I have) or TIA 15.1 (same version as the documentation and file extension say is required). I can't even tell it to ignore that and discard all hardware that requires it or open it read-only. All I can do in that dialogue is select cancel. |
2/28/2024 5:07 AM | |
Joined: 9/21/2012 Last visit: 4/27/2024 Posts: 3930 Rating: (444) |
You need Startdrive installed also, since it's referring to G series drives. |